Communication with s7-315
#2
Hello,
the ISO on TCP will be the right choice for communication with a S7-315.
To connect, you have to set up the IP adress of your plc in the communication settings, the TSAP schoul be 3/2.
If you have only one plc, you can set the IP adress completely like 192.168.100.22, if you have more plc´s in your network, you can set the IP adress like 192.168.100.0 and then set the station number in the VDF to 22 and to the other ending values of the other plc´s. The station number will be added to the last value of the IP adress that you will get the complete 192.168.100.22 out of these settings.
You can read and write datablocks, marker words, input and output words without any changes in your plc program.
There is no gsd file for the Tia portal.
Ralph Ringel
Vertrieb / Support
Tel: +49 (0)2631 941288-35
Antworten


Nachrichten in diesem Thema
Communication with s7-315 - von scarebyte - 14.11.2014, 11:37
RE: Communication with s7-315 - von R.Ringel - 19.11.2014, 10:17